tbedford
Mechanical
- Jul 11, 2004
- 79
I am commissioning a dual fuel natural gas/oil hydronic boiler by Bryan Boilers. Input MBH is 1200/600 and output is 1002 MBH. Boiler MAWP is 160 psig.
I have attached a photo of PRV installed on top of boiler. Intuitively, a reduction in size from 2" to 3/4" orifice represents a significant blockage in the event of over-pressurization.
My experience and education has always been the PRV inlet size matches the boiler size.
I can't find a code reference for the PRU inlet piping... lots of reference for the PRV discharge.
I have also attached boiler nameplate.
Thank you, Tom