Pressure Relief

Status
Not open for further replies.

Jimbob73

Mechanical
Aug 27, 2003
6
Are there any standards (UK), codes, or guidance notes available for enclosure over pressure relief design for fire suppression systems?
 
Replies continue below

Recommended for you

I have dealings with IRI (Industrial Risk Insurers) when installing ovens and heaters in the auto plants. Each one of these pieces of equipment must meet IRI's approval before installing, and one of the things that they deal with is explosion relief for enclosures, and their standard is: 1 Square Foot of relief for every 15 Cubic Feet of enclosure as a minimum. Hopefully this helps, but then again I am dealing with gas and the products of combustion.

 