Dear all,
As we are complying to NFPA standards as close as possible, one of the confusion starts is with NFPA 20 2019 Annex A A.14.2.6 (4):
Fire Pump Settings. The fire pump system, when started by
pressure drop, should be arranged as follows:
(a) The jockey pump stop point should equal the pump
churn pressure plus the minimum static supply
pressure.
Assuming that our pump churn pressure will be 14 Bar, and minimum static supply remains 0, our final jockey pump stop point shall be at 14 bar.
However, when crossing over to NPFA 13 rules, the sprinkler pipeline pressure shall not exceed 175 PSI (12.1 Bar). In this case, how can we formulate a pump pressure setting that will comply both NFPA standards?
I also understand the provision of PRV's to regulate this pressure back to 12.1 Bar, but if the PRV's keep relieving pressure constantly in the system pipeline, wouldn't the jockey pump re-activate constantly?
Thanks all
As we are complying to NFPA standards as close as possible, one of the confusion starts is with NFPA 20 2019 Annex A A.14.2.6 (4):
Fire Pump Settings. The fire pump system, when started by
pressure drop, should be arranged as follows:
(a) The jockey pump stop point should equal the pump
churn pressure plus the minimum static supply
pressure.
Assuming that our pump churn pressure will be 14 Bar, and minimum static supply remains 0, our final jockey pump stop point shall be at 14 bar.
However, when crossing over to NPFA 13 rules, the sprinkler pipeline pressure shall not exceed 175 PSI (12.1 Bar). In this case, how can we formulate a pump pressure setting that will comply both NFPA standards?
I also understand the provision of PRV's to regulate this pressure back to 12.1 Bar, but if the PRV's keep relieving pressure constantly in the system pipeline, wouldn't the jockey pump re-activate constantly?
Thanks all