1. Sorry, I should have said "pump". Go with the Enerpac pump!
2. That is small diameter wire (non-stranded)! You may be looking at custom grip chucks for such small diameter. PRECISION-SURELOCK have 0.25" multi-use chucks, but anyhting small and it will be custom. PRECISION have fabricated custom chucks for me - from very small to very large (2"). Contact Stan Landry at PRECISION and he will help you. I am assuming you are in the US.
3. The following photo is of the components that make up a small stressing set-up:
4. The following photo is how a multi-use chuck would grip a 7-wire strand on the back of a hollow centre ram:
You will need 2 multi-use chucks for each prestressing wire - one for each end. You will pre-cut your prestressing wire with one end say 2 or 3 feet longer for purposes of stressing each wire, so you need one additional multi-use chuck for stressing...BUT, stressing with a hollow centre ram you are going to require a 'nose' with a recess on the leading edge so that when you stress the wire chuck wedges can displace a small distance - if the wedges cannot 'slip' freely during stressing then you will not correctly stress the wire/s.
5. Your precast bed length is very short (10 feet), so the effective prestress force you obtain after accounting for losses is going to be significant. for example, if you 'seat' the chuck wedges for each wire and loose say 1/4" of seating loss you have lost a high % of total elongation over the 10 foot bed length. Also, you need to look at wire slippage and the 'development length' at the ends - these will effect your prestress force.
6. Stressing is a dangerous operation. I encourage you to obtain the services of an experienced person who understands all safety and operations of prestressing. Just