- Sep 15, 2003
- 224
I am working on upgrading an old boiler installation in a large site. The utility building boilers ( 3 off x 5mW each) serve 6 different buildings through a tunnel under the site. There are primary and secondary pumps but it was origionally 3 port valves on the secondary side. Most have been changed out to 2 port over the years. There is 2 differential pressure sensors going into 2 off the building and the sec. pumps ramp up/down to to maintian the worst case. The set point is 2 bar.
The problem is even in the middle of last winter the boilers are only running a half duty with 3 of them ON and the delta T is only 10 Deg C, the design Delta T is 25 deg C. The sec. pumps have not really ramped down a whole lot since winter and now i am in summer. OK the site is a manufacturing and hot water is used in some processes but the delta T now is only 5 deg C... but maintenance want ot keep all boilers on.
With the low Delta T is looks like one boiler can do the job but if i turn off the other 2 boilers it is too much water from the sec loop to get thro the running boiler...mind you I dont knwo how much water is in the sec loop for sure... I got it check with ultra sonic but i dont believe it 100%... I was very high...
Am i missing something...maybe I have to check the site for more by pass valves and more 3 port valves that need changing...
Maybe the differential pressure set point is too high although 2 bar DP between F&R going into a building does not seem to high either but i might drop it and see if there is any complaints...this will slow down the sec. pumps. Iwas going to close off 1 bulding at a time and see which building give the biggest chaneg in system pressure..
Any tips...??
The problem is even in the middle of last winter the boilers are only running a half duty with 3 of them ON and the delta T is only 10 Deg C, the design Delta T is 25 deg C. The sec. pumps have not really ramped down a whole lot since winter and now i am in summer. OK the site is a manufacturing and hot water is used in some processes but the delta T now is only 5 deg C... but maintenance want ot keep all boilers on.
With the low Delta T is looks like one boiler can do the job but if i turn off the other 2 boilers it is too much water from the sec loop to get thro the running boiler...mind you I dont knwo how much water is in the sec loop for sure... I got it check with ultra sonic but i dont believe it 100%... I was very high...
Am i missing something...maybe I have to check the site for more by pass valves and more 3 port valves that need changing...
Maybe the differential pressure set point is too high although 2 bar DP between F&R going into a building does not seem to high either but i might drop it and see if there is any complaints...this will slow down the sec. pumps. Iwas going to close off 1 bulding at a time and see which building give the biggest chaneg in system pressure..
Any tips...??