I'm involved with the replacement of the diesel genset on a 480V high resistance ground system.
As part of the project, a Schweitzer SEL-547 distributed generator interconnection relay is replacing several individual relays protecting the utility interconnection breaker. The OLD relays were all connected using two VT's in an open delta configuration.
The SEL-547 needs a four wire wye voltage input, and is designed for a direct connection to a 480V system without VT's, which initially sounded quite convenient. However, we were advised against such a connection in an HRG system. Something about the neutral begin unusable.
The recommended solution was to connect three VT's in a delta-to-wye configuration, thus providing a four wire wye output to connect to the relay. In order to supply 480 volts L-L on the secondary, a VT ratio of 1.73:1 was needed. The only VT's readily available at that ratio were actually labeled for 208:120 V service.
This scheme was wired up and the primary 2A fuses were closed with the secondary fuses open. The VT's heated up quickly and either two or three of the primary fuses blew.
Is the problem simply from using the VT's above their design voltage, or is there something more complex at work here?
Thanks,
John
As part of the project, a Schweitzer SEL-547 distributed generator interconnection relay is replacing several individual relays protecting the utility interconnection breaker. The OLD relays were all connected using two VT's in an open delta configuration.
The SEL-547 needs a four wire wye voltage input, and is designed for a direct connection to a 480V system without VT's, which initially sounded quite convenient. However, we were advised against such a connection in an HRG system. Something about the neutral begin unusable.
The recommended solution was to connect three VT's in a delta-to-wye configuration, thus providing a four wire wye output to connect to the relay. In order to supply 480 volts L-L on the secondary, a VT ratio of 1.73:1 was needed. The only VT's readily available at that ratio were actually labeled for 208:120 V service.
This scheme was wired up and the primary 2A fuses were closed with the secondary fuses open. The VT's heated up quickly and either two or three of the primary fuses blew.
Is the problem simply from using the VT's above their design voltage, or is there something more complex at work here?