kingnero
Mechanical
- Aug 15, 2009
- 1,776
I am doing a study of a welding machine that is to be used "in the field".
The generator is a 3 phase+N (3x400V) 12 kVA - 8.8 kW Honda Europower,
which turns out to be a bit underpowered when starting with welding - you can hear the engine stutter.
The welding machine is a Miller 350 XMT invertor, used for MIG welding at 28V - 160-200 Amps.
P=sqrt(3) x 28 x 180 = 8.7 kW, is this correct for an invertor? the efficiency not taken into consideration.
I am mostly interested in the welding part, however if the generator isn't good enough than that is also my problem. I know the basics about electricity, but I have no experience with gensets.
Could anybody help me out here?
I will try next week hooking up a large light on the gen, so that it won't need to start from stationary when welding (reducing the "lag", I hope).
Should I buy a 3-phase "energy analyzer" (or how it might be called in english), that gives direct reading of the three line voltages and currents, power factor, frequency, ... to check for the inrush and continuous current,
or will that only indicate what I think (genset is underdimensioned), or are there other tips and tricks that might be interesting for this particular case ?
The generator is a 3 phase+N (3x400V) 12 kVA - 8.8 kW Honda Europower,
which turns out to be a bit underpowered when starting with welding - you can hear the engine stutter.
The welding machine is a Miller 350 XMT invertor, used for MIG welding at 28V - 160-200 Amps.
P=sqrt(3) x 28 x 180 = 8.7 kW, is this correct for an invertor? the efficiency not taken into consideration.
I am mostly interested in the welding part, however if the generator isn't good enough than that is also my problem. I know the basics about electricity, but I have no experience with gensets.
Could anybody help me out here?
I will try next week hooking up a large light on the gen, so that it won't need to start from stationary when welding (reducing the "lag", I hope).
Should I buy a 3-phase "energy analyzer" (or how it might be called in english), that gives direct reading of the three line voltages and currents, power factor, frequency, ... to check for the inrush and continuous current,
or will that only indicate what I think (genset is underdimensioned), or are there other tips and tricks that might be interesting for this particular case ?