Can someone tell me/or point me to a web site that I can get information on figureing out the proper size fuse for engine block heaters like those used on emergency generators.
 
Replies continue below

Recommended for you

Consult the manufacturer and the applicable local building codes.

A typical 5kW heater might be rated 240 volts. 5000/240 = 20.8A. For NEC areas, 20.8 x 1.25 = 26.0, so you would need 30A fuses.
 