I would like help protecting the motor with the following data on the name plate:
MOD : MGA 6811
NA : 1679410707
HP : 1400
RPM : 1487
Hertz : 50
VOLTS : 6900V
AMPS : 103.7A
DUTY : S1
INSULATION : F
IL/IN : 7
SF : 1.15
COS : 0.88
AMB : 50°C
FTM : RISE 70°C
We have an Motortronics MVC3 Soft Starter & a Multilin 369 Relay.
For the MVC3 I need help understanding the Setpoint Page 8 settings.
My understanding is that the LRA is 700A.
SP8.1 & SP8.2 has the run curve locked rotor time & start curve locked rotor time set to the overload curve selected in SP1.3
Are these the time I read under 7FLA on the overload curve?
What acceleration time limit, number of starts per hour and time between starts would you recommend?
As for SP.12 Do I read the time for the cold and hot stall time from the overload curve under 7FLA?
Now going to the 369 Relay
How do I choose the VT ratio needed under Setpoint 2?
Do I need to match the S3 running cool time constant and stopped cool time constant to that selected in the MVC3 SP.12?
Should I also match the S3 hot/cold safe stall ratio to that of the MVC3 SP.12?
Should I also match the S5 start inhibits to those selected in the MVC3 SP.8?
As for S7 over/underfrequency, what is the acceptable deviation from the 50Hz acceptable?
Should I match this to the one selected on the MVC3 SP3.11?
MOD : MGA 6811
NA : 1679410707
HP : 1400
RPM : 1487
Hertz : 50
VOLTS : 6900V
AMPS : 103.7A
DUTY : S1
INSULATION : F
IL/IN : 7
SF : 1.15
COS : 0.88
AMB : 50°C
FTM : RISE 70°C
We have an Motortronics MVC3 Soft Starter & a Multilin 369 Relay.
For the MVC3 I need help understanding the Setpoint Page 8 settings.
My understanding is that the LRA is 700A.
SP8.1 & SP8.2 has the run curve locked rotor time & start curve locked rotor time set to the overload curve selected in SP1.3
Are these the time I read under 7FLA on the overload curve?
What acceleration time limit, number of starts per hour and time between starts would you recommend?
As for SP.12 Do I read the time for the cold and hot stall time from the overload curve under 7FLA?
Now going to the 369 Relay
How do I choose the VT ratio needed under Setpoint 2?
Do I need to match the S3 running cool time constant and stopped cool time constant to that selected in the MVC3 SP.12?
Should I also match the S3 hot/cold safe stall ratio to that of the MVC3 SP.12?
Should I also match the S5 start inhibits to those selected in the MVC3 SP.8?
As for S7 over/underfrequency, what is the acceptable deviation from the 50Hz acceptable?
Should I match this to the one selected on the MVC3 SP3.11?