- Nov 29, 2011
- 20
We Have two Station Service Transformer (SST) to supply our 6,3 kV Station Board A&B on a Coal fired Power Plant. The SST rating is 150 / 6,3 kV and primary side (150kV) supplied from the 150 kV transmission line through GIS (Gas Insulated Switchgear). There was a black out on the system so the SST completely loss the voltage. but on that fault the 6,3 kV Station board incoming CB didn't Trip. The station board itself provide with Bus Under Voltage (27) protection Relay and it works after the SST loss the voltage. But The trip contact did not connencted to the incoming breaker.
My quenstion is : is that a standard that the incoming CB must trip because off loss voltage of the SST (like my example)? because we are affraid of accidental energization if the Transmission line suddenly energize and the station board incoming CB still at close position and all the load are connected. It will shock the busbar.
My quenstion is : is that a standard that the incoming CB must trip because off loss voltage of the SST (like my example)? because we are affraid of accidental energization if the Transmission line suddenly energize and the station board incoming CB still at close position and all the load are connected. It will shock the busbar.