protection sizing for distribution transformer

Status
Not open for further replies.

prdpks2000

Electrical
Aug 2, 2020
16
is some one can provide rules for sizing transformer HV protection breaker sizing, I get some basic details through the following link
Link
 
Replies continue below

Recommended for you

A good starting point is 125% of the maximum rating of the transformer. If this is a utility substation transformer with temperature monitoring, they often go higher. It will also depend on the type of tranformer and the type of primary protection. Most MV fuse manufacturers publish tables of recommended fuse sizes for different transformer sizes. And any applicable local codes, of course.
 
Thanks ,
I checking some consulting manual per it current of transformer with rated MVA at lowest tap link of same
Link
 