I'm looking for some type of reference that supports producing a watertight construction joint by sandblasting or water jetting the surface of the first pour to 1)remove laitance, 2)provide roughness, and 3)enable the new pour to bond directly to the first pour's exposed aggregate.

My application is liquid manure storage structures, usually 6' - 12' in depth with 8" - 12" thick concrete walls. Most states require waterstops in such joints which some consider unnecessary.

Thank you.
 
Replies continue below

Recommended for you

Don't forget that concrete shrinks. That's why there are either sawed joints or, as in your case, separate pours to make a place for shrinkage, rather than some random cracks developing.
 
I agree a water stop is required.

What about a sealant groove detail on the inside?

Does anyone have a good detail for sewage exposure?

For potable water we often use backing rod and sika "goop" to fill the void, but for sewage exposure not sure this detail works?
 