jimmy2times
Electrical
- Jun 26, 2007
- 138
We have a couple of diesel generators and gas turbine on a ship. The class society guy wants us to prove the integrity of reverse power relays as part of his intermediate (2.5yr) survey. He suggested other operators choose to actually induce a real reverse power situation by taking load off one set and driving the set frequency up on the other so as to motor the unloaded generator. What is general view out there on this? I would have thought less risk of damage to just get a contactor in and make protection tests on the relay without the generator running.