Prressure Treated Wood Retaining Wall

Status
Not open for further replies.

andyfabian

Structural
Jul 2, 2003
33
I have a retaining wall that requires a redesign. The contractor originally constructed the wall without a design. It was constructed of 6x6 pressure treated lumber in (approximately) 8 feet sections. Every so often a dead man was placed using 6x6's also. The inadequacy was mainly due to poor construction of the wall as well as non-compacted soil conditions.

Now that it collapsed, the contractor realizes the worth of an engineer. Since I am asked to take responsibility for the retaining wall, it needs to be done correctly. I am familiar with the idea of this design, but would like to have a design guide to reference.

Thanks in advance.
 
Replies continue below

Recommended for you

Hey boo1, thanks for the reply. I am having problems finding the information at that link. If you could elaborate, I would greatly appreciate it. Although, I think we are on the same page, let me note that the wall is a freestanding retaining wall. Other than fixity at the base (or not - depending on the design), the only restraint is due to deadmen. This is not a house (i.e. there is no floor at the top to provide support).

Thanks,

Andy
 
Andy - I have an old US Steel Catalog (in Adobe Acrobat format) that has design information on retaining walls with and without tieback systems. If you need it quickly, will be happy to e-mail it to you. Another option - the information is available on an L.B. Foster Co. piling catalog (on CD). You can request the CD at
 
Are you planning a soldier pile and lagging wall, or cribbing? How tall is it? Location? Soil conditions? Any site restraints?

[pacman]

Please see FAQ731-376 by [blue]VPL[/blue] for tips on how to make the best use of Eng-Tips Fora.
 
1. Cribbing
2. 11 feet
3. Northern DE
4. Will be replacing soil with well drained backfill such as stone if necessary
5. 15 feet from the face of the wall to the edge of property line on the backside of the wall
 