Hi all,
According to WSDOT Getechincal Design Manual(6.5.3.1), horizontal pseudo-static coefficient Kh=0.5*PGA, the PGA at Everett, WA is 0.3, so I think Kh is 0.5*0.3=0.15.

But I read some getechnical reports, Kh=0.5*0.3*1.18=0.177 was used in these reports. what does 1.18 mean?

Thanks
 
Replies continue below

Recommended for you

wshi,

Suggest you contact the author of the reports containing the 1.18 factor...

Jeff


Jeffrey T. Donville, PE
TTL Associates, Inc.

The views or opinions expressed by me are my own and do not necessarily reflect the views or opinions of my employer.
 

Probably it's the soil amplification factor, variable according to stratigraphic sequence:

the formula would go: Kh = Ag/g * S for foundations, and
Kh = 0.5 Ag/g * S for retaining walls, S stands for Soil (amplification).

I'm answering based upon european EC8 guidelines, but I saw in IBC and NEHRP the rationale is the same.
 
wshi,

The 1.18 is the soil amplification factor. It is used to take the peak bedrock acceleration (PBA) to peak ground acceleration (PGA) and is used to account for site soil amplification. The PBA in Everett is 0.3. The PGA is 0.354.