Hi,
I have a few questions regarding the orientation of PSV discharge. Medium is dry air. No insulation, No heat trace, and PSV discharge open to the atmosphere.
Reference API 520 Part 2 Section, the PSV venting to the atmosphere is generally vertically up with a weather cap, low point drain, and a support at the elbow. In all the below cases the support is present. No issue on the piping stress side. However, there are other concerns:
1= Due to extremely cold temperatures (-45C) and snow blowing vent up is not suitable. It can fill up with snow. The low point drain is also expected to freeze up and not function as intended due to temperature variations.
2= The second recommended orientation is to vent vertically down. Again stress-wise no issue. But when the relief valve operates it will blow over the vessel. In winter, the vessel is expected to have snow on top of it and during the relief valve operation, the snow can dislodge and fall onto the nearby person. A possible safety concern.
3= Third recommendation is to have the discharge vent horizontally straight with a 45-degree cut at the end, and the cut facing down. This will prevent any rain/snow accumulation and due to free-draining, no risk of blockage. Additionally having a birdcage to prevent any bird entry. The issues with this 3rd recommendation are:
==A) The exact dimensions of the bird cage are unknown. If not done correctly, it can come off and with the speed of discharge air, it can be a safety risk. Or restriction to the flow at the time of operation.
==B) There is building/piping infrastructure on all four sides of PSV with the closest one at 1m. I cannot find if there is any recommendation in the code regarding the free space distance in the direction of PSV discharge.
Any recommendation on what should be done in such a scenario?
I have a few questions regarding the orientation of PSV discharge. Medium is dry air. No insulation, No heat trace, and PSV discharge open to the atmosphere.
Reference API 520 Part 2 Section, the PSV venting to the atmosphere is generally vertically up with a weather cap, low point drain, and a support at the elbow. In all the below cases the support is present. No issue on the piping stress side. However, there are other concerns:
1= Due to extremely cold temperatures (-45C) and snow blowing vent up is not suitable. It can fill up with snow. The low point drain is also expected to freeze up and not function as intended due to temperature variations.
2= The second recommended orientation is to vent vertically down. Again stress-wise no issue. But when the relief valve operates it will blow over the vessel. In winter, the vessel is expected to have snow on top of it and during the relief valve operation, the snow can dislodge and fall onto the nearby person. A possible safety concern.
3= Third recommendation is to have the discharge vent horizontally straight with a 45-degree cut at the end, and the cut facing down. This will prevent any rain/snow accumulation and due to free-draining, no risk of blockage. Additionally having a birdcage to prevent any bird entry. The issues with this 3rd recommendation are:
==A) The exact dimensions of the bird cage are unknown. If not done correctly, it can come off and with the speed of discharge air, it can be a safety risk. Or restriction to the flow at the time of operation.
==B) There is building/piping infrastructure on all four sides of PSV with the closest one at 1m. I cannot find if there is any recommendation in the code regarding the free space distance in the direction of PSV discharge.
Any recommendation on what should be done in such a scenario?