niallPOC
Mechanical
- Jun 27, 2007
- 3
I have an application where I am installing a pressure safety valve on the discharge pipework of an air compressor to protect the piping from overpressure. The PSV is located close to the compressor in the plant room but it is necessary to pipe the discharge of the PSV to outside the room to reduce noise in the plant room. The PSV will be an L orifice valve with a DN80 inlet and DN100 outlet. In order to keep cost down, I want to use a convential spring operated valve, not a bellows type and therefore am calculating the built-up back pressure in the discharge piping during venting to ensure it is not greater than 10% of the valve set pressure.
The difficulty I am having is calculating this built up back pressure. If I use a DN100 pipe for the discharge piping, with the flow rate at 14190kg/hr, which the valve is rated for, as the air expands down to atmospheric pressure through the discharge pipe it will easily reach sonic velocity and flow will be choked. Therefore I have looked at using DN150 pipe for the discharge piping with a DN100 to DN150 enlarger immediately downstream of the valve. To calculate the back pressure with this arrangement I have tried setting the exit pressure of the discharge pipe to atmospheric. However with the minimal pressure drop through the DN150 section of piping and a increase in pressure which occurs through the enlarger, the calculation is telling me choked flow will occur at the inlet of the enlarger.
I have been referring to API521/ISO23251 to help understand the sizing methodology and using FFDS 2.5C and standard isothrmal calculation sheets to calculate pressure drop.
I am stuck on the following basic points;
1 - For flow which is sub-sonic, i.e. not choked and capable of achieving full flow rate required, is setting the exit pressure from the discharge pipe at atmospheric pressure and working back to calculate back pressure at the valve the right approach?
2 - To calculate this is using Isothermal flow equation a suitable approach? The problem it generates is that the static pressure increases significantly through the enlarger. Is this realistic?
3 - If a PSV is rated for 14190kg/hr and greater, but has a DN100 outlet, will flow not choke in the outlet of this valve without any discharge piping, assuming that the air will be at atmospheric pressure right at the exit of the valve?
The difficulty I am having is calculating this built up back pressure. If I use a DN100 pipe for the discharge piping, with the flow rate at 14190kg/hr, which the valve is rated for, as the air expands down to atmospheric pressure through the discharge pipe it will easily reach sonic velocity and flow will be choked. Therefore I have looked at using DN150 pipe for the discharge piping with a DN100 to DN150 enlarger immediately downstream of the valve. To calculate the back pressure with this arrangement I have tried setting the exit pressure of the discharge pipe to atmospheric. However with the minimal pressure drop through the DN150 section of piping and a increase in pressure which occurs through the enlarger, the calculation is telling me choked flow will occur at the inlet of the enlarger.
I have been referring to API521/ISO23251 to help understand the sizing methodology and using FFDS 2.5C and standard isothrmal calculation sheets to calculate pressure drop.
I am stuck on the following basic points;
1 - For flow which is sub-sonic, i.e. not choked and capable of achieving full flow rate required, is setting the exit pressure from the discharge pipe at atmospheric pressure and working back to calculate back pressure at the valve the right approach?
2 - To calculate this is using Isothermal flow equation a suitable approach? The problem it generates is that the static pressure increases significantly through the enlarger. Is this realistic?
3 - If a PSV is rated for 14190kg/hr and greater, but has a DN100 outlet, will flow not choke in the outlet of this valve without any discharge piping, assuming that the air will be at atmospheric pressure right at the exit of the valve?