Hello everyone,
I used Korf to simulate a PSV opening at 9300 kPag to estimate the back pressure in the flare line.
This PSV protects a separator against blocked flow.
The instantaneous flow through the orifice is close to 150 MMSCFD. Yet the blocked flow case for this PSV is only 70MMSCFD, it seems like the PSV will release at a rate of 150 MMSCFD for a brief moment as it opens.
Does this make sense to you? and does this mean the entire downstream system has to be designed with this maximum release? even though the normal blocked flow is only half of that?
Or is it possible that the volume of piping in the flare line may act as a buffer against this instantaneous flow rate and actual back pressure be less?
Thank you for your help!