CKwan
Mechanical
- Feb 21, 2013
- 3
I needed to calculate a mixed air temperature so I used the formula and found the number. To double check my numbers, I used the McQuay Psychrometric Analyser, but the number was different. I was a bit confused so I got the psychrometric chart and did a manual calculation by drawing a straight line across the two points. I realized that the drawn line cut across the saturation line. If the line cut across the saturation line, does the straight line method still stand, or does it require a different method to calculate the mixed air temperature?
Below are some sample numbers:
O/A temp: -40F
O/A flow: 4615 cfm
R/A temp: 90F
R/A flow: 10385 cfm
Calculated MAT: 50F
McQuay calculated MAT: 42.3F (assuming everything is 50%RH)
How would you find the mixed air temperature in this case?
Below are some sample numbers:
O/A temp: -40F
O/A flow: 4615 cfm
R/A temp: 90F
R/A flow: 10385 cfm
Calculated MAT: 50F
McQuay calculated MAT: 42.3F (assuming everything is 50%RH)
How would you find the mixed air temperature in this case?