DEL2000
Structural
- May 10, 2004
- 48
In section 9.2 of the sixth edition of PTI's Post-tensioning manual, they have a step number 5B - Calculate Post-tensioning force using "allowable average compression". I realize that this step isn't a code enforced step of the design, but more of a rule of thumb (an unwritten rule, to be exact, but more on that later) to prevent problems from restraint from shrinking. Are there any other reasons why you should limit the average compression (P/A) on your sections?
But as for these "allowable average compression" limits, I could find no where in this manual where it spells what they should be directly. Does anybody have a reference with these values with discussions as to why they are important? How about just simple guidelines used in your respective offices?
I have a pretty good idea . . . 150 psi minimum everywhere (1 way slabs, 2 way slabs, beams), 100 psi for temperature and shrinkage tendons, where used. The minimums are pretty easy.
I guess I am mostly interested in what the maximums are roughly. I believe that slabs (both one way and two way), should be on the order of 250 to 300 psi maximum. What about beams? Can you go up to 500 psi on beams?
Long story short . . . I have a beam that works, a transfer beam supporting four stories of structure above. I am stage stressing it, its overall average precompression (just on the beam web, discounting the flange because I am lazy) is 460 to 530 psi. These beams work pretty comfortably, shear works pretty easily, doesn't require too much flexural steel, deflection is good. So I was looking at the possibility of using a shallower section, since we used a good portion of the ceiling space. The only thing that I am hesitant about is going too much higher on the P/A . . . but I can't find any concrete guidelines on where you should limit yourself too.
Thanks for any help that you can provide.
But as for these "allowable average compression" limits, I could find no where in this manual where it spells what they should be directly. Does anybody have a reference with these values with discussions as to why they are important? How about just simple guidelines used in your respective offices?
I have a pretty good idea . . . 150 psi minimum everywhere (1 way slabs, 2 way slabs, beams), 100 psi for temperature and shrinkage tendons, where used. The minimums are pretty easy.
I guess I am mostly interested in what the maximums are roughly. I believe that slabs (both one way and two way), should be on the order of 250 to 300 psi maximum. What about beams? Can you go up to 500 psi on beams?
Long story short . . . I have a beam that works, a transfer beam supporting four stories of structure above. I am stage stressing it, its overall average precompression (just on the beam web, discounting the flange because I am lazy) is 460 to 530 psi. These beams work pretty comfortably, shear works pretty easily, doesn't require too much flexural steel, deflection is good. So I was looking at the possibility of using a shallower section, since we used a good portion of the ceiling space. The only thing that I am hesitant about is going too much higher on the P/A . . . but I can't find any concrete guidelines on where you should limit yourself too.
Thanks for any help that you can provide.