Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pull out Fuse at VT Drawer in MV SWGR

Status
Not open for further replies.

CuriousElectron

Electrical
Jun 24, 2017
184
Hey Gents,
This may be a silly question. I was looking at the VT drawer and noticed that there is a pull out block containing the low-voltage fuses at the front of the Instrument Voltage Transformer drawer(cubicle). What is the function of this device - is it simply to disconnect the circuit for isolation purposes?

Thanks,
EE
 
Replies continue below

Recommended for you

Overcurrent protection for the PT secondary?

-JFPE
 
Nominally overcurrent protection for the VT secondary, but in reality a means of disconnecting the VT from sources of back energization. VT fuses are part of nearly ever clearance. Low-side fuses are both easier and safer to remove than high-side fuses.