I've worked myself into a circular reasoning of death here. Help.
I'm starting in a phase 2 of sorts of someone else's design and project. The gist is this, the former principle mechanical engineer ran a really rough 1st draft of hydraulic calculations to spec a new pump and a new flow control valve for estimate purposes. He assumed 20 psi dp at max flow rate (water, 1600 gpm) across the control valve. He then used this pressure drop in addition to the line losses and static heads to size the pumps.
Fine
Now insert me into this project..
To do the next round of estimates, I have to "tighten" up the calculations to get more accurate quotes on equipment.
I recalculate the line losses using the 3D models of piping with accurate dimensions, so far so good, the head loss is slightly different as expected. But now I turn to the control valves and I'm thinking, man, I really need to get an accurate dp across these so that I can more accurately size my pumps.
Here is the chicken and egg problem. As far as I can tell, you size a control valve using a specified dp across it (the difference between your pump outlet pressure and your final destination pressure). But, I don't have this in reality because I'm basing my pump head off of bogus control valve dps in the first place. (I'm referencing the Emerson/Fischer literature on the standard method of specing a control valve. In other words, I calculated my pump dp based on a control valve dp (that came out of someone's imagination), so I can't very well use my pump dp to calculate my control valve dp without circular reasoning.
How do I get out of this conundrum?
*Known information is max and min flow requirements as well as piping diameters.
I'm starting in a phase 2 of sorts of someone else's design and project. The gist is this, the former principle mechanical engineer ran a really rough 1st draft of hydraulic calculations to spec a new pump and a new flow control valve for estimate purposes. He assumed 20 psi dp at max flow rate (water, 1600 gpm) across the control valve. He then used this pressure drop in addition to the line losses and static heads to size the pumps.
Fine
Now insert me into this project..
To do the next round of estimates, I have to "tighten" up the calculations to get more accurate quotes on equipment.
I recalculate the line losses using the 3D models of piping with accurate dimensions, so far so good, the head loss is slightly different as expected. But now I turn to the control valves and I'm thinking, man, I really need to get an accurate dp across these so that I can more accurately size my pumps.
Here is the chicken and egg problem. As far as I can tell, you size a control valve using a specified dp across it (the difference between your pump outlet pressure and your final destination pressure). But, I don't have this in reality because I'm basing my pump head off of bogus control valve dps in the first place. (I'm referencing the Emerson/Fischer literature on the standard method of specing a control valve. In other words, I calculated my pump dp based on a control valve dp (that came out of someone's imagination), so I can't very well use my pump dp to calculate my control valve dp without circular reasoning.
How do I get out of this conundrum?
*Known information is max and min flow requirements as well as piping diameters.