jimhokie
Mechanical
- Feb 16, 2005
- 50
The pump is a horizonally mounted, closed impeeler, single stage, end suction dual volute, top centerline discharge centrifugal pump, 1800 RPM, 12" suction and discharge.
The service is a chilled water pump that circulates cold water from an AC plant. It initially runs with no mechanical seal leakage, but once the chiller is turned on and the water drops below about 50°F, the seal starts to leak. When the chiller is turned off and the water rises back to ambient (~70°F), the leakage remains. Once the pump is left idle over night, it starts up with no leakage the next morning until the chillers are turned on and the water drops below 50°, then the leakage returns and repeats the pattern. Cycling the pump off/on after the water warms back up doesn't stop the leakage...only sitting overnight does. We’re puzzled as to why the leakage remains when the chiller is turned off and the water warms up above 50°--if it’s thermal pipe strain, it seems this should be relieved once the pipe warms back up to ambient. Perhaps there’s some hysteresis in the pipe strain that relieves itself over night due to structural vibrations or other longer term effect.
I suspect there is likely some static strain preexisting as a result of bad piping alignment, which is then exacerbated by the relatively small temperature change when the chillers are turned on, enough to distort the casing, causing shaft strain and the seal leakage.
At this point, it is impractical to break the piping connections to verify piping alignment. Any other ideas for confirming if static and/or thermal piping strain could be causing the leakage, or any thoughts on what else the problem could be? Both the seal and pump manufacturers are stumped.
The service is a chilled water pump that circulates cold water from an AC plant. It initially runs with no mechanical seal leakage, but once the chiller is turned on and the water drops below about 50°F, the seal starts to leak. When the chiller is turned off and the water rises back to ambient (~70°F), the leakage remains. Once the pump is left idle over night, it starts up with no leakage the next morning until the chillers are turned on and the water drops below 50°, then the leakage returns and repeats the pattern. Cycling the pump off/on after the water warms back up doesn't stop the leakage...only sitting overnight does. We’re puzzled as to why the leakage remains when the chiller is turned off and the water warms up above 50°--if it’s thermal pipe strain, it seems this should be relieved once the pipe warms back up to ambient. Perhaps there’s some hysteresis in the pipe strain that relieves itself over night due to structural vibrations or other longer term effect.
I suspect there is likely some static strain preexisting as a result of bad piping alignment, which is then exacerbated by the relatively small temperature change when the chillers are turned on, enough to distort the casing, causing shaft strain and the seal leakage.
At this point, it is impractical to break the piping connections to verify piping alignment. Any other ideas for confirming if static and/or thermal piping strain could be causing the leakage, or any thoughts on what else the problem could be? Both the seal and pump manufacturers are stumped.