Quick question:
I have emergency fire pumps (diesel and electric) that are rated at 136 psig maximum and the controls are set to maintain the discharge header at 149 to 159 psig using the jockey pumps, the electric fire pump is set come on at 144 psig and the diesel at 134 psig. Our construction EPC has told us that the controls are set this to address the head in the water tank that supplies water to the fire system.
Essentially, they are telling us the set points are higher than the pump curve to account for the extra head in the tank. Does it make sense for the pump to be set to come on at a pressure higher than its rating?
Thanks,
Ray
I have emergency fire pumps (diesel and electric) that are rated at 136 psig maximum and the controls are set to maintain the discharge header at 149 to 159 psig using the jockey pumps, the electric fire pump is set come on at 144 psig and the diesel at 134 psig. Our construction EPC has told us that the controls are set this to address the head in the water tank that supplies water to the fire system.
Essentially, they are telling us the set points are higher than the pump curve to account for the extra head in the tank. Does it make sense for the pump to be set to come on at a pressure higher than its rating?
Thanks,
Ray