Hello,
I have a pump system that is giving me some headaches and I can't figure out why. This pump is controlled by a VFD, because the load varies quite a bit. The VFD has been set up to vary the pump speed in order to maintain a constant pressure. The pressure sensor is downstream from a non-return valve.
The whole thing works quite well when valves are open. The problem is when all valves are closed. The system was designed so that when the VFD slows down to around 40% of its maximum speed for 15 seconds it goes into sleep mode. The idea here is that if all valves are closed the VFD keeps slowing the pump down to maintain the pressure setpoint until it reaches a point where it can turn off. The non-return valve ensures that pressure is kept in the pipe so that the VFD does not cycle from being in sleep mode to run mode.
The problem here is that the VFD is not going into sleep mode when the valves are closed. There are no leaks and there is no water flow, but the pump just keeps pumping in order to maintain the pressure. Because there is no water flow the impeller is overheating.
Originally we thought it was the programming in the VFD but that has been tested and proven to work.
Any help would be greatly appreciated. I have installed a number of similar systems to this and never had these problems.
I have a pump system that is giving me some headaches and I can't figure out why. This pump is controlled by a VFD, because the load varies quite a bit. The VFD has been set up to vary the pump speed in order to maintain a constant pressure. The pressure sensor is downstream from a non-return valve.
The whole thing works quite well when valves are open. The problem is when all valves are closed. The system was designed so that when the VFD slows down to around 40% of its maximum speed for 15 seconds it goes into sleep mode. The idea here is that if all valves are closed the VFD keeps slowing the pump down to maintain the pressure setpoint until it reaches a point where it can turn off. The non-return valve ensures that pressure is kept in the pipe so that the VFD does not cycle from being in sleep mode to run mode.
The problem here is that the VFD is not going into sleep mode when the valves are closed. There are no leaks and there is no water flow, but the pump just keeps pumping in order to maintain the pressure. Because there is no water flow the impeller is overheating.
Originally we thought it was the programming in the VFD but that has been tested and proven to work.
Any help would be greatly appreciated. I have installed a number of similar systems to this and never had these problems.