Pump tripping out

Status
Not open for further replies.

oldfitter

Mechanical
Oct 19, 2010
12
0
0
GB
On a 2 pump sewage pumping station, one of the pumps trips out occasionally. Once it is manually reset, it can be started and will pump. Telemetry reports reveal the pump seems to "fail" and send out an alarm 5 minutes after it has stopped. The pump has been split to see whether it is blocked but never is. The pump amps when it runs are ok. Both the pumps autorotate duty, but only one pump ever fails. The electricians cant, wont fault find as they say they need to be present when the fault occurs. I could understand the pump tripping while in operation, but why 5 minutes after it has stopped ?

Any ideas

Thanks
 
Replies continue below

Recommended for you

What is the actual sensor that sends out the "fail" alarm? Do you have continuous readings on amps? What do they do right at the time of failure?
 
You might pass on to the electrician to turn of the rock music, then it will not trip out.