Pump Upstream Higher Pressure Issue 1

Status
Not open for further replies.

nuuvox000

Mechanical
Sep 17, 2019
344
0
16
US
pumps_jienyh.png


This is how I'd like to pipe in a new heat exchanger into the existing building system. The pump shown is variable speed. I'm concerned that the higher pressure HWS upstream water will push more water through the pump than required when the pump is running at low speed. Do you think this will be an issue? Curious if the pump will "resist" the additional turning of the impeller if the upstream pressure is trying to push water through, when it's running. Thanks in advance!
 
Replies continue below

Recommended for you

One more thought: I wonder if I should put the circuit setter next to the open/close valve to make sure we're not sending way too much water from the supply to return pipe. Like so:
rev3_uuwqbp.png
 
you don't need a balancing valve or circuit setter. You control pump speed based on temperature. And the temperatures will fluctuate (either based on demand, or you main loop will fluctuate).
 