Hello all!
Looking for some thoughts on a bit of a code grey area if anyone has any prior experience. I'm working on a two-way PT flat slab with a fairly high concrete strength 60 MPa (8700 psi for the US folk) and I'm currently working through the punching shear calculations. Here are the code equations that are relevant to the design (Based on ACI 318-19, leaving out the extra column dimension equations for simplicity in comparison):
Table 22.6.5.2: For two-way members without shear reinforcement,
vc = 4*sqrt(f'c)
where sqrt(f'c) is limited to 100 psi (f'c = 10,000 psi).
Section 22.6.5.5: For prestressed, two-way members conforming to 22.6.5.4, vc shall be permitted to be:
vc = 3.5*sqrt(f'c) + 0.3*fpc + Vp/(bo*d)
where f'c is limited to 70 psi (f'c = 4900 psi).
The concrete strength being used is in between the sqrt(f'c) limits of 70 and 100 psi, which brings up our lovely code grey area.
The wording of the prestressed equation says "shall be permitted" which leads me to believe it is intended to be an additional equation to increase punching shear capacity due to precompression (makes some sense). However, since the prestressed equation limits the maximum concrete stress to a lower value, at low levels of precompression, it actually reduces the shear capacity of the slab, compared to the non-PT equation (!!!).
So I've got a couple of options at this point, and I'm not sure which makes the most sense:
1. Use the PT equation, limiting the concrete strength to 4900 psi
2. Use the Non-PT equation, limiting the concrete strength to 10000 psi
3. Use the Non-PT equation, limiting the concrete strength to 4900 psi
Any thoughts? Appreciate it!
vc = 4*sqrt(f'c)