ThePunisher
Electrical
- Nov 7, 2009
- 384
Hi all,
I have a customer with 300 KW PV inverter system and they are planning to interconnect such to the grid. Their equiopment is not IEEE 1547 or UL 1741 tested for grid intertie.
I am thinking that if their inverter capacity or maximum output is less than the peak load or the inverter output can reduce current output during light loading to prevent export to utility, then it would eliminate complicated requirements for interconnection. However, is there an inverter that does that?
Alternatively, I was also thinking about splitting the PV-fed AC panelboard from normal utility panelboard and apply open transition tie contactors in the event PV is insufficent to power local loads. But I am looking for a seamless way of connecting inverter and utility without exporting so that the PV system is only for minimizing utility import only.
Regards
I have a customer with 300 KW PV inverter system and they are planning to interconnect such to the grid. Their equiopment is not IEEE 1547 or UL 1741 tested for grid intertie.
I am thinking that if their inverter capacity or maximum output is less than the peak load or the inverter output can reduce current output during light loading to prevent export to utility, then it would eliminate complicated requirements for interconnection. However, is there an inverter that does that?
Alternatively, I was also thinking about splitting the PV-fed AC panelboard from normal utility panelboard and apply open transition tie contactors in the event PV is insufficent to power local loads. But I am looking for a seamless way of connecting inverter and utility without exporting so that the PV system is only for minimizing utility import only.
Regards