With all due respect, I am concerned about possible long-term ramifications of some comments made on this thread. If as some say a plastic pipe system is good for good long-term performance desired by an Owner even if short-term defection is far greater than 5%, why then have standards and a great many significant local specifications for many decades limit deflection?? Another reason for my skepticism was I once attended a paper/presentation many years ago where some researchers at least initially sort of lauded a very deep test installation (I think in Pennsylvania) of both corrugated and smooth-lined, profile-walled plastic pipes, and I believe then even postulated a theory that primarily inward compressive creeping behavior of the plastic (the pipe reportedly ended up being a smaller diameter than it started out!) helped to reduce the heavy earth load. It appeared the intent of this paper (and I later found out similar papers by the same folks in multiple other engineering forums) was to promote some sort of rather high strain plastic/new design behavior phenomena, and I guess perhaps even thereby the use of similar plastic pipes for deep cover installations. If I remember correctly, this particular test piping was VERY carefully bedded with very select materials and bedding/compaction was also VERY carefully inspected/tested, and I’ll note this pipeline at least short-term generally deflected LESS than 5%, I guess as a result of same.
I subsequently also attended a paper/presentation of some competitive (not the same) researchers a few years later, who said that while the original researchers promised some longer-term follow-up of this installation the original reports, it was they instead who along with some other folks walked through this same piping installation just a few years later, inspected this installation, and they were thus reporting on the actual longer-term results. They reported that while the line was not generally severely deflected, the line exhibited “several interesting conditions”, including: “1. Buckling of the inner liner of the smooth lined pipe.” And “2. Circumferential cracking at the inside crest of the corrugated pipe.” They noted that the various pipes in this installation apparently buckled in a couple different directions and/or manners, and they even described buckling as “severe”. There was apparently cracking near every joint of pipe, at least one location not near a joint nor even under the deepest cover, and water was observed infiltrating the very carefully installed test line. While I will note this test installation was of polyethylene pipe (normally most used for drainage), I am not sure exactly how any other similarly creeping plastics would be dependably insulated long-term from similar behaviors (and I also happened to notice above the reference/warning of “local buckling” also from stanier). The newer authors also stated at the end of the newer paper, “Experience from other installations of polyethylene drainage pipe indicate that this type of buckling occurs at more normal depths.”
With regard to the inference in posts that pipe deflections even up to 20% are from a theoretical standpoint somehow acceptable, and while I can’t remember all specific details of problems, I am further very skeptical (even if a plastic pipe WALL happened to survive without long-term bucking or cracking) that all joints would maintain their integrity in a pipeline subject to such magnitude, unpredictable wall movements.
With all due respect, and while I don’t doubt something close to this may have been accomplished in a controlled test installation somewhere, forgive me that I am also very skeptical of the general statement that in practice an installed, unpressurized gravity flexible plastic (subject to creep) pipe will all of a sudden simply stop deflecting say once it reaches 5% or 7.5% deflection in 30 days or less. I believe this is contrary to some experience (and maybe even common sense!)
While I guess I sort of understand the intent of after-the-fact sort of exculpatory statements that deflections far greater than 5% or 7.5% are acceptable (an attempt to help the parties at least initially sleep better, to prevent at least very early re-installation expense that must be borne by somebody, and/or at least initially prevent uncomfortable, embarrassing, and/or hostile contract disputes etc.??), in the long run I would nevertheless be very cautious based on what little I have seen/published to step outside this box/standard of care, lest one (as I heard a colleague of mine in forensic pipe work once say in perhaps a little of an overstatement, in referring I think to some similar very flexible pipe experiences) be in essence “burying their own Chernobyl”.
I suspect some or all of the actual papers concerning what I am talking about in this post can probably be obtained/accessed by anyone for their own reading/consideration at nominal cost, through e.g. ASCE or other publications service with a keyword search. I noticed also some time ago that are also some multiple interesting pictures of perhaps similar, apparently actual installed plastic pipe wall conditions now on the Caltrans site at
(e.g. see Section “5.1.4 Plastic Pipe”).
If anyone cannot independently find what they want in this regard, I would be happy to try to dig out some more detailed reference information to help locate – please let me know on this thread if this is needed.