It appears at least some USA manufacturers of polyethylene pipe are indeed promoting specifications requiring field hydrotesting per ASTM F2164. You can read at least the overview/entre' to the latest version of this standard,, and certainly purchase same if you wish and are responsible for knowing the details therein, at the portal
It appears a historical 2002 version of this standard, not controlled as I believe there is a 2013 version available, can even be read for at least the time being at
A few points to consider in looking at what is meant by field testing of pipelines. The most common basic types of piping used for water service, including polyethylene, pvc and ductile iron all go back to near WWII or thereabouts. However, it is some interesting that while I'm sure various manufacturers and AHJ's have had their own and likely differing opinions concerning same, no sort of widespread utility consensus USA field testing protocols for plastic water pipes e.g. ANSI/AWWA standards have really been available until quite recent years.
1. Note first from the aforementioned first portal that this web page for ASTM F2164 leads off with the statement, "5.1 If required by the authority having jurisdiction, hydrostatic pressure leak testing may be conducted to discover and correct leaks or faults in a newly constructed or modified polyethylene or crosslinked polyethylene pressure piping system before placing the system in service.") While the the very first prepositional phrase of this ad (I believe verbatim from a "Significance and Use" section of the original F2164 standard circa 2002) appears to indicate that field hydrostatic testing of pipelines is optional, in my opinion a well-run field hydrostatic test on a new pipeline is instead absolutely critical to provide some degree of protection for all parties to any pipe material piping design and installation, and ultimately the tax/rate payers. This language may be contrasted e.g. with that e.g. of ANSI/AWWA C600 for ductile iron piping systems that reads more unequivocally in Sec. 5.1.2 Workmanship, "All pipe and appurtenances shall be installed and joined in conformance with this standard and tested under pressure for defects and leaks in accordance with Sec. 5.2 of this standard..." then per Sec. 5.2.1.2, "...Following the installation of any new pipe or any valved section thereof shall be subjected to a hydrostatic pressure test." [I would particularly note e.g. that per AWWA C906 governing requirements for USA polyethylene pipe manufacture, individual polyethylene pipes are not required to be pressure tested by the manufacturer/at the factory, not even considering all that conceivably can happen to the pipe later/before final installation and burial!]
2. This as well as the criteria from the linked document bimr provides seems quite liberal in the overall scheme of things. Lets say we are going to test a normal new 2,000 feet long 8" diameter underground water distribution pipe line that has been fully installed in the buried position it is intended to serve, and in our first case say it is polyethylene pipe to be field tested say to 160 psi.When I pull up the "Technical Note 802" on the website at
the first thing I see are all kinds of caveats with regard to tests and exactly what tests do and do not mean (though I wonder a little bit why, that is another story and I'll not worry about that here). As I know my required test pressure is 1-1/2 times my maximum service pressure, I will choose "Alternate 2", that I see is lead off with, "Immediately following the initial expansion phase, monitor the amount of make-up water required to maintain test pressure for one (1), or two (2), or three (3) hours. If the amount of make-up water needed to maintain test pressure does not exceed the amount in Table 2, no leakage is indicated." I choose 2 hours duration, as I know from my experience that that has long been the MINIMUM required/vetted for many years duration of AWWA C600 (for other material), so I look at their "Table 2 Test Phase – Alternate 2 – Make-Up Water Allowance". I see that for my two hour test the allowable make-up water is 1.0 U.S. gallon for every 100 feet of 8" pipe in my testing extant. For my 2,000 feet long project, I thus run the not too hard calculation (2,000 ft/100 ft)(1.0 Gal.) and come up a full 20 gallons (most of the bottom half of a 55 gal drum) of water they say I should allow the Contractor to pump back into this small hdpe pipeline if necessary to maintain pressure etc. Let’s now look at case two, that I had chosen instead ductile iron pipe for this project. Looking at Table 11-6 of AWWA M41, AWWA C600 (or tables in any number of major utility testing specifications re-created there from on the web) you will find that at 160 psi the testing allowance to maintain pressure is no more than 0.77 U.S. gallons per hour testing duration per 1,000 feet of pipeline involved (meaning I must multiply this amount by (2,000 ft/1,000)(2 hr/1 hr) ft or 4 to get the total testing allowance for such modern ductile iron piping installation that is in fact ~3.1 gallons, or milk jugs, of water). Now before we proceed further, let me add some more information, also from AWWA standards. Unlike ductile iron pipe, some folks may not know plastic pipe manufacturers are not now necessarily required by minimum AWWA standards e.g. AWWA C906 to hydrostatically leak or pressure strength test each piece of pipe at the factory, and I daresay little or no for hdpe water pipe is likely so tested. Also and on the other hand, anyone who has been around field installations of pipes very long understands that reasonable field testing allowances from the practical standpoint are necessary for the real world. It is virtually impossible to make sure all pipelines are laid precisely like profile lines on a CAD drawing, or that air release devices end up located precisely at every high point as shown on drawings (so that no air is trapped in pipelines), said air goes into and out of solution as it will, temperatures heating or cooling over the test duration have an effect on pressure (particularly on trapped air in accordance with Boyles, Charles, and Gay Lussacs etc.), pipes can settle or move at least slightly as they are pressurized (changing test volume some), water can soak at least a little into e.g. cement mortar linings, and indeed particularly for hdpe pipes there is also some rather complex change in test volume due to Poisson as well as Bourdon behaviors of the viscoelastic material (that are frankly more dependent on the pipe embedment and layout, as well as variations in piping, than some numbers in a table!) etc. In other words, pumping 3 gallons of water back into a ductile iron pipeline or seven times that allowable amount back into a polyethylene pipeline (the latter claimed outrageously by the vendors to be "jointless" and "leak-proof")"after the same two hour test doesn't mean either one of them has leaked that amount of water.