For once we've got a project where I get to specify the CTs rather than just making do with whatever is already there.
The CTs will supply a low-impedance transformer diff relay and I want to specify class PX so that I can ask for a high enough knee point to avoid saturation as much as possible.
I've worked out the fault level, X/R, secondary lead resistance, relay burden etc, but then I get stuck. To specify a suitable Vk for the CT I need to know what the CT secondary resistance is. How do I know what is a reasonable maximum secondary resistance to specify?
I've checked out test certificates from some similar older 5A CTs and it works out to be about 8 mOhm per turn - would this be a reasonable value for a 1A CT or would they use thinner wire to fit in more turns?
Also - is it still common practice to install separate cores for separate protection relays (we're also got a directional relay) or is it acceptable to now supply everything from the same core?
Can anyone recommend a good book on this?
The CTs will supply a low-impedance transformer diff relay and I want to specify class PX so that I can ask for a high enough knee point to avoid saturation as much as possible.
I've worked out the fault level, X/R, secondary lead resistance, relay burden etc, but then I get stuck. To specify a suitable Vk for the CT I need to know what the CT secondary resistance is. How do I know what is a reasonable maximum secondary resistance to specify?
I've checked out test certificates from some similar older 5A CTs and it works out to be about 8 mOhm per turn - would this be a reasonable value for a 1A CT or would they use thinner wire to fit in more turns?
Also - is it still common practice to install separate cores for separate protection relays (we're also got a directional relay) or is it acceptable to now supply everything from the same core?
Can anyone recommend a good book on this?