As a second follow up,
Yes, you can use QR heads in NFPA 13 as well as residential heads, but at the cost of a larger design area and more heads in the design area, than that required when using residential heads in a residential application.
The NFPA 13 residential design requirement is 4 heads regardless of walls for design, while the QR design could be largest room, or more likely an area/density design. In addition, there is no hose allowance required for residential design, while a hose allowance is likely required for a QR design.
There, hope that was clear as mud.