Gents,
I am in the process of putting a heattreat facility together for stainless and alloy steels. It will be a l x w x h--- 30'x6'x 5'
It looks like the level will be around 48"Dp to allow for displacement.
I am thinking of using the same size tank as a cold tank recirculating the fluid from the cold tank to the cooling tower & quench tank.
I am thinking a 7 - 10 hp pump 300 gpm to change quench tank volume in a 1/2 hour.Is this fast enough??
My question is if i dip 8,000 lbs of 1900 deg f steel into a tank of fluid(water)or (oil) at 90 deg f how much temp rise should i expect.
I need to keep it below 115 deg f.
I need to size one cooling tower for water and one for oil and i don't want to oversize them.
Thanks to everyone for your time,Joe