question in hydraulic calculation
zicoo000
15
hi every body
I have two lines Feed my project at 8 bar , the first line feed for the landing valve
and other feed zone's and fire hose reel.
in hydraulic calculation of zone sprinkler neglected 7 bar of landing valve ??? or what can i do
pleas advice
as per NFPA 13, the calculation must be performed for each system (Standpipe, sprinkler and etc) and not in combination of two systems. In case you are calculating sprinkler system in hydraulic calculation, you don't need to consider the standpipe connection as a standpipe demand but only a hose allowance.
GeorgeMech,
Thankful for your response
George,
That's not always the case. For a building with a LH or OH-1 or OH-2 discharge density combined with a Class I standpipe, the standpipe can be more hydraulically demanding. I currently have a sprinklered 27 high rise on my desk with 3 standpipes. The 1,000 GPM @ 100 PSIG at the highest floor is far more demanding than any on the OH-1 or LH discharge densities.
Stookeyfpe,
Yes it is true and most of the cases standpipe system is more demanding compared with sprinkler system, my statement is only to clarify the question of zicooo regarding on combining the standpipe system and sprinkler system in calculation, although, NFPA also states that if the building is partially sprinklered, you must combined the two system in order to get the system demand.