27
Hi, we have a 2000KVA delta-wye 23KV/460V Oil filled transformer (T-1) feeding a 225KVA, delta-wye 460V/230V transformer (T-2) inturn feeding 3phase air conditioning equipment and lighting. Our cables and wires are color coded right from the LV side of T-2 up to the downstream panelboards' branch circuits. My question is . . . how do I change the phase sequence without disturbing the color coding of cables & wires. I intend to switch any two connections of the T-2 windings. Shall the switching of connections be in the primary or secondary? I'm sure there are experts out there who can provide the correct or appropriate solution. Thanks.
 
Replies continue below

Recommended for you

Switching any two phases, primary or secondary will change the phase sequence on the secondary.

I assume you realize that this will cause ALL of your 3-phase motors to rotate in the opposite direction. This is a much bigger concern than color coding of the phase conductors. Just use colored tape next time - it's a lot easier to swap.
 