Stewie_
Civil/Environmental
- Aug 18, 2010
- 16
Hi, Dear All,
AASHTO LRFD 2014 sec 3.10.9.2 tells that "For all other sites in Zone 1, the horizontal design connection force in the restrained directions shall not be less than 0.25 times the vertical reaction due to the tributaiy permanent load and the tributaiy live loads assumed to exist during an earthquake."
Is this tributary dead/live load should be factored?
If it is, then the factored EQ becomes
gamma_EQ*0.25*(gamma_DL*R_DL+gamma_LL*R_LL).
Or it should be
gamma_EQ*0.25*(R_DL+R_LL).
This is about fixed pier dowel design. I just don't feel good using the load factors twice.
Please help.
Thanks,
Stewie
AASHTO LRFD 2014 sec 3.10.9.2 tells that "For all other sites in Zone 1, the horizontal design connection force in the restrained directions shall not be less than 0.25 times the vertical reaction due to the tributaiy permanent load and the tributaiy live loads assumed to exist during an earthquake."
Is this tributary dead/live load should be factored?
If it is, then the factored EQ becomes
gamma_EQ*0.25*(gamma_DL*R_DL+gamma_LL*R_LL).
Or it should be
gamma_EQ*0.25*(R_DL+R_LL).
This is about fixed pier dowel design. I just don't feel good using the load factors twice.
Please help.
Thanks,
Stewie