Question on Equipment Specs
rsr32
22
I have the spec sheet from a sanyo split cooling system , and am a bit confused as far as the power input specification:
"Cooling Capacity (BTU/h): 17,500(4,000-17,500)
Power Input (W) : 1500/1500(250-1500)"
I'm assuming the 1500W is for peak @ 17,500BTU/h and the 250W is for the 4000BTU/h operating capacity??
Similarly, on ceiling mounted units,
"Cooling Capacity (BTU/h): 39,000(9,500-39,000)
Power Input (W) : 3890/3830"
and my assumption doesn't seem to hold in this case?? or are the two numbers representing inside unit and outside unit (evaporator/condenser unit)
what am I missing here?
TIA,
Is this part of the specs? (Sanyo split system ductless AC, 17000 BTUH)
? Power Supply Voltage/Phase/Hz: 230/208V / 1PH / 60Hz
? Running AMPS (Cooling) : 7/7.7 (1.2?7.7) Variable Speed
? Fuse or Circuit Breaker Capacity: 20
If so, your max power is approx 4.6 KW assuming 100% power factor.
how do you come to the 4.6kW max power? why is that number different than the "power input" and what about the ceiling mounted unit which is a 39,000BTUH unit? sorry for all the questions, I'm a bit confused, and thanks for your help
Assuming 100% power factor, watts = volts x amps = 230 x 20 = 4600 (Maximum) Actual running kw is about 230 x 7.7 =1771 watts.
Anoying indeed to have a manufacturer publish performance data for the electrician and not for the engineer.
The solution in such cases: Change manufacturer. Try Mitsubishi, they will give you the nice data that you need.