Mila15
Electrical
- Dec 19, 2012
- 27
My question is regarding a branch breaker in a large 480v Power Panel. The circuit feeds a 36A heating load. Can a 40A breaker be used, knowing the following:
- This is at a small generating Station
- Space Heater is supposed to turn on only when ambient temperature is below 50F (10C)
- #8 AWG cable is rated for 90C, but rated for 50A (about 140% of load) at 75C insulation
Thanks!
- This is at a small generating Station
- Space Heater is supposed to turn on only when ambient temperature is below 50F (10C)
- #8 AWG cable is rated for 90C, but rated for 50A (about 140% of load) at 75C insulation
Thanks!