jheidt2543
Civil/Environmental
- Sep 23, 2001
- 1,466
I put forth the following examples regarding the wind load charts in the IBC 2000 Building Code. In Table 1609.6.2.1 (2) Component and Cladding Loads for a Building with a Mean Roof Height of 30 Feet Located in Exposure B:
Example 1: If I have a wall system with girts at 6’ center-to-center and column spacing of 25’ center-to-center, the contributing area (effective wind area) for a girt would be 6’ x 25’ = 150 sf. If I’m in a wall Zone 5, with a basic wind speed of 90 mph, then Table 1609.6.2.1 (2) gives wind load values of +12.4 psf and -15.1 psf, based on Note a.
Example 2: If in the same wall system as Example 1, I install 6” metal studs at 16” on center x 8’ high, below the first girt, then the contributing area (effective wind area) for the stud would be 1.33’ x 8.0’ = 10.64 sf. For the same conditions as in Example 1, the wind load values would be +14.6 psf and -19.5 psf.
Example 3: For the same conditions above, with a building eave height of 20’, the building columns would be sized based on a contributing area (effective wind area) of 25’ x 20’ = 500 sf. From Table 1609.6.2.1 (1) Main Wind Force-Resisting System Loads for a Building with a Mean Roof Height of 30 Feet Located in Exposure B, the wind loads transferred to the columns from a wall End Zone with a Roof Angle of 0 to 5 deg., the wind load would be 12.8 psf.
So for the same wall surface with the same wind blowing, there are three different positive wind loadings, 12.4, 14.6 and 12.8 AND two negative loads -15.1 and -19.5. Is this correct? Also, am I interpreting the column under the C&C Table labeled Effective Wind Area correctly?
Are you all actually refining your designs this much, or do you just take the highest positive value and the highest negative value and use them through out? You don’t change girt sizes between the end panel and the middle of a building side wall do you?
Example 1: If I have a wall system with girts at 6’ center-to-center and column spacing of 25’ center-to-center, the contributing area (effective wind area) for a girt would be 6’ x 25’ = 150 sf. If I’m in a wall Zone 5, with a basic wind speed of 90 mph, then Table 1609.6.2.1 (2) gives wind load values of +12.4 psf and -15.1 psf, based on Note a.
Example 2: If in the same wall system as Example 1, I install 6” metal studs at 16” on center x 8’ high, below the first girt, then the contributing area (effective wind area) for the stud would be 1.33’ x 8.0’ = 10.64 sf. For the same conditions as in Example 1, the wind load values would be +14.6 psf and -19.5 psf.
Example 3: For the same conditions above, with a building eave height of 20’, the building columns would be sized based on a contributing area (effective wind area) of 25’ x 20’ = 500 sf. From Table 1609.6.2.1 (1) Main Wind Force-Resisting System Loads for a Building with a Mean Roof Height of 30 Feet Located in Exposure B, the wind loads transferred to the columns from a wall End Zone with a Roof Angle of 0 to 5 deg., the wind load would be 12.8 psf.
So for the same wall surface with the same wind blowing, there are three different positive wind loadings, 12.4, 14.6 and 12.8 AND two negative loads -15.1 and -19.5. Is this correct? Also, am I interpreting the column under the C&C Table labeled Effective Wind Area correctly?
Are you all actually refining your designs this much, or do you just take the highest positive value and the highest negative value and use them through out? You don’t change girt sizes between the end panel and the middle of a building side wall do you?