Well, Bill. We were quite a lot of people that were surprised to see this. And the instrumentation to see the phenomenon was not even there. The tell-tale sign was an unstable induction motor. It is a long story, that I shall keep as short as possible.
I was a commissioning engineer at Siemens back in the early seventies. At that time, there were no fast frequency inverters, so the test rig for fast compressors that I was starting up had Ward-Leonard systems that fed a DC motor with a multi-pole three-phase generator. The WL system excitation was controlled by a PWM DC amplifier which was controlled by a standard speed controller.
I was fairly young at that time. But had been working with variable drives in the Swedish Army, at ASEA (now ABB) and Siemens for almost ten years, so I thought that I had seen it all already (little did I know).
Anyhow. I couldn't make that drive stable. It oscillated constantly with a low amplitude and a rather high frequency - something like 10 Hz, if I remember correctly.
Nothing could stabilize it. All the standard tricks were of no use. I finally replaced the speed controller with a fixed voltage source that excitated the WL directly. Oscillation still there. To rule out the suspicion that the WL was unstable 'in sich' (sorry, German company), we got ourselves a set of forklifter batteries and ran the DC motor from that. Oscillations still there. Munich was now engaged (the system had been designed there) and a Doktor-doktor plus a staff of technicians arrived with a van full of instrumentation.
A very thorough test followed. One interesting test was to record the speeds of the generator and the induction motor. We clearly had an unstable system. It was ringing loud and clearly and the 'steady state' assumption inherent in the speed/torque curve of the induction motor was scrutinized in detail. Hey! This was research - and I loved it.
The quick fix this time was to add inductance in the only available path, the connection between generator and induction motor. The inductance consisted of three 35 mm2 Cu cables that were laid in coils with 50 turns and around 600 mm diameter. Not that we really could prove mathematically that it would work. It was what was available and it worked the first time.
The DOL overshoot is something I could see on a much later occasion. I shall look for that recording. Or, if necessary, make another one. The instrumentation to do it is much more userfriendly these days. Problem: Finding an induction motor with an encoder that is DOL started (the motor, I mean).
Gunnar Englund
--------------------------------------