JStephen said:If the reports in question just said everything was okay when it wasn't, is that a "falsified" report? Was there some kind of scheming going on with those reports, or just failure to recognize or call out problems?
rowingengineer said:Call me crazy but I always like to have the guy who designed the building also to be the inspector.
They found that the Harmon's third-party inspection firm, Monrovia, Calif.-based Converse Consultants, falsified 62 daily reports between March and July of 2008 stating that things were OK when they weren't. County inspectors missed the problems, too. It seems rebar was misplaced inside link beams that transfer horizontal loading to the building's shear walls. A shear wall is a braced panel wall that counters lateral loads on a structure. In other words, it supports the building and keeps it from falling over.
Stirrup hooks, ties that hold rebar together, also were spaced incorrectly, county investigators found; some even poked past the floor slab, prompting workers to cut them off with a blowtorch so they wouldn't show.
"We do not see this very often," county building official Ron Lynn said. "They installed it wrong. That's the bottom line."
Harmon's design called for pouring top portions of the 8-foot-thick link beams with the floor slab, which is a tricky procedure given the tight and exact spacing of rebar.
Harmon workers reportedly moved rebar without first getting an OK from the structural engineer, Halcrow Yolles, which is a major no-no in the construction chain of command. Rebar placement is carefully configured to maximize structural building strength.
"Congestion, or too much rebar matted together, prevented proper coverage and distribution of concrete," said a project official who requested anonymity.
Perini counters that structural drawings for Harmon "were months late and contained many errors and omissions," adding that MGM Resorts "would have to acknowledge that the permitted set of drawings never matched the sets of drawings (used) to construct the project."
paddingtongreen said:A personal note; I hated working on jobs implementing the designs of "Great Architects".