CraigRochester
Mechanical
- Sep 21, 2006
- 10
I'm working on a project to evaluate the best way to sequence loads for power outages in a pharmaceutical production facility.
We have:
[ol][li]Two independent main feeds from the power company @ 13.8 KV[/li]
[li]"Tie Breaker" switchgear that switches all power to the active feed upon loss of one.
[/li]
[li]Step down transformers for 4.6KV(chillers),480 V, and other low voltage services.[/li]
[li]Backup generator for selected equipment[/li]
[li]UPS service to selected equipment: all control systems and local PLCs[/li]
[li]Control systems monitor the generator's automatic transfer switch(ATC) and initiate power loss response[/li]
[/ol]
Our current sequence of operations for responding to power loss is to initiate shutdown of all controlled equipment whenever the ATC output contacts for power loss close.
My question is: Can I bridge the brief(exact time being determined) period when the "Tie-Breaker" switchgear transfers without initiating a full shutdown sequence. If so, could you provide guidance on how to evaluate the systems' capability to experience a quick power loss.
Thanks,
Craig
We have:
[ol][li]Two independent main feeds from the power company @ 13.8 KV[/li]
[li]"Tie Breaker" switchgear that switches all power to the active feed upon loss of one.
[/li]
[li]Step down transformers for 4.6KV(chillers),480 V, and other low voltage services.[/li]
[li]Backup generator for selected equipment[/li]
[li]UPS service to selected equipment: all control systems and local PLCs[/li]
[li]Control systems monitor the generator's automatic transfer switch(ATC) and initiate power loss response[/li]
[/ol]
Our current sequence of operations for responding to power loss is to initiate shutdown of all controlled equipment whenever the ATC output contacts for power loss close.
My question is: Can I bridge the brief(exact time being determined) period when the "Tie-Breaker" switchgear transfers without initiating a full shutdown sequence. If so, could you provide guidance on how to evaluate the systems' capability to experience a quick power loss.
Thanks,
Craig