Is there a document that furnishes the test pressure that the refrigerant piping has to be subjected to in the case of a DX system using R22 refrigerant ?

HVAC68
 
Replies continue below

Recommended for you

Hi HVAC68,

I have attached an extract from the CIBSE Design Specification for DX Air Conditioning Equipment in Buildings. Table 29. If you didnt know already the table shows HCFC22, this is R22.

Regards

Gunner777
 
 http://files.engineering.com/getfile.aspx?folder=75f9425e-0c8a-4c7f-bcb5-50044e78e2a1&file=Recomended_R22_Test_pressures_(HCFC22).doc