NFPA 13 2002 EDITION States
8.16.5 Hose Connections.
8.16.5.1.3 Hose connections shall be supplied from one of
the following:
(5) In rack storage areas, the ceiling sprinkler system in the same area (as long as in-rack sprinklers are provided in
the same area and are separately controlled)
Does this mean if I have a Rack system(valve controled Riser) supplied from the bottom of the 6" riser that covers dericly over the racks, I can supply the hose valves from that system?
Also can someone tell me, if I supply the rack system off the bottom of the (E) 6" riser with new control valve and flow switch do I have to calc both systems flowing together?
Can I just calc the racks per FM Global Standards @ 8 sprinklers in one level @ 30 psi and leave the Clg. Sprinkler system @ .60/2000.
Thanks for everything