I cant understand this math. ive been over and over it. Each time I get a little further, then I loose it again.

ref:
How to calculate rafter thrust? -Help! at

Can someone help me figure cable load?

4/12

24" rafter spacing.

No rafter ties at all. A few existing collar ties.

ceiling joists run parallel to ridge.

house is 27' x 30'(ridge).

7/8" roof planking and asphalt shingles.

thanks,
pa
 
Replies continue below

Recommended for you

1/2 * vertical reaction at rafter support * run / rise

Very simple statics problem.
Do a free body diagram of one rafter (there is no vertical support at the ridge)
 
huh?

ref: Do a free body diagram of one rafter (there is no vertical support at the ridge)
 
There is horizontal support at the ridge. So you can calculate all that you need to know.

BA
 
that helps, thanks.

ref: There is horizontal support at the ridge. So you can calculate all that you need to know.
 