RC frame - large beam on small columns?

Status
Not open for further replies.

greznik91

Structural
Feb 14, 2017
186
Im dealing with a RC frame building. There is a RC slab above - 200 mm thick.


MODEL_3D_klnaum.png



RC slab:

PLATA_xjqlsx.png


Columns supports are pinned.
All connections between column - beam are modeled as a moment connection.
That mean that bending moment is transfered from end of the beam to a column.
Based on spans I think my yellow columns are pretty small in cross section dimensions (300/1000 mm)
I have made some calculations and its barely OK but my gut feeling is not good at all.

Your opinion?

Also - since columns/walls are pretty close together, I think the best way to go is to make continuous footings instead of spread footings connected with foundation beams.
 
Replies continue below

Recommended for you

Your column seems to be robust enough... is it marginal because you are transferring a high moment? Can you use a transfer moment equal to DL + maybe 30% of LL? Done lots of parkades where I've used a LL = 15psf for alternating loading and moment transfers at columns.

Dik
 
I'd be inclined to design the beam as though it were pinned at each end. Moment transfer into the narrow columns might be questionable.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
It all starts with a good estimate on the cracked stiffness of the members in question. But even that can vary so I usually take a couple of passes based on the range(s) of possible stiffness. Checking the joint wouldn't hurt either.

 
The beam is 600x500 and the columns are 300x1000. Increase the beam width to 1000 to match the column. Design the beam as per KootK's recommendation, i.e. wL[sup]2[/sup]/8 at midspan, but supply top steel for wL[sup]2[/sup]/24 each end.

BA
 
Do you need RC-frames for horizontal loads? Since there is a stair opening im guessing that its not 1-floor structure.
That beam with 9 m span and 50 cm height doesn't look convincing...

(Are you working with Eurocodes? your software looks like Radimpex)
 
thanks for help

Yes, I need RC frame for horiz. loads (earthquake).
The beam is 60/60 cm.

Yes im working with Eurocodes and software Tower.

 
If you are taking horizontal loads you are not allowed to redistribute bending moments.(EC2 5.5 (6))

I would:
- assume all connections with beams/columns/walls as pinned (and still add upper rebar for the fixing moments), so no frames.
- use longer walls as cantilevers for horizontal loads. hopefully there is a basements, if not than I would "insert" this moments into strip footings

I hope it helps..
 
Thanks for answer Tommy385

EC2 5.5 (6) states: 'For the design of columns the elastic moments from frame action should be used without any redistribution.'

I have been thinking to design columns based on a moment from envelope ( moment I got from modal analysis and from ULS(so I dont know what kind of redistribution you were thinking about).

There is no basement, so yes, I agree, I have been planning to do strip footings anyway.

 
I meant this..
dik (Structural)20 Aug 18 13:28
Your column seems to be robust enough... is it marginal because you are transferring a high moment? Can you use a transfer moment equal to DL + maybe 30% of LL? Done lots of parkades where I've used a LL = 15psf for alternating loading and moment transfers at columns.

 