mjevans
Electrical
- Aug 18, 2003
- 5
Hello out there. Can anyone help with this problem. I have a bank of resistive heater elements that by design also present a capacitive load to earth, protected by a 30mA RCD (ELCB). Here is my question, I assume that the current in the neutral is the resistive current only, whilst the line current will be the vector sum of the resistive and capacitive currents. The RCD will trip on the difference of these two currents. Is this the case? For the circuit outlined above, I have measured Ires = 2.4A and Icap =0.188A (I have also read that a 30mA device can trip at much lower currents, is the rated figure the worst case scenario?). I look forward to your comments!