Confirm your your startup and operations requirements: (pressure, temperature, cleaniless, etc.) and then verify your "normal" startup procedure.
Confirm you "can do" that sequence.
Open and inspect the interior of ALL piping and equipment: Manually if possible, with see-snakes and TV video and pigs and inspection ports and handway ports.
Confirm that erosion and corrosion and failues are not present in the out-of-way places.
Confirm ALL valves and instrument (1) still exist, still can be controlled, and still physically oeprate.
Bring ALL instruments out of the unite units and thermowells and pits and "open and inspect" ALL instrument boxes and panels, and ALL instruments and controls are back in calibration. (You will need to walk down your P&ID's while doing this - because the "Oh Yeah! I forgot we put that one in backwards" factors have been been forgotten.
Confirm ALL controller programming and instrument control function actually still work: Assume a few are NOT Y2K compliant, a few will only run on DOS, a few are not Windows 95 compliant, a few are ONLY Windows 95 compliant and can't run under the new operating systems and graphics.
Have your startup team SEPARATELY run THEIR simulations and control and accident and shutdown and emergency routines on a simulator.
Have your electrical team walk down ALL boxes and cables - look for rats, mice, badgers, porcupines and anteaters, as well as elephants and kangaroo nests. Meggar test ALL motors and power cables and transformers.
From your P&ID, plan your startup flush and "wet-down" sequence so there are no leaks and surprises.
Confirm ALL rigging and cranes and elevators and manlifts are certified.