rjgoebel
Electrical
- Jun 10, 2005
- 40
This was an interesting issue I ran into while doing a fault study for a hospital. We turned out to be about 3kA over the 35kA AIC rating of an existing chiller. This rating was mostly constricted by a couple parts within the starter , (CB and contactor) that were only rated at 35kA. I was looking into different ways to get this issue resolved...
1 - to reduce the available fault current seen by the chiller
2 - to increase the AIC of the chiller.
Our recommendation as a firm is going to end up being to supply new VFD starters for these chillers. After looking into using a line reactor to reduce the fault current seen by the chiller, an app engineer told me that these reactors can only be used when a VFD is existing and will reduce the seen fault current by max of 5%. I really have no feel for these reactors and what they do, and when you would want to use them by and large.
I have heard many times of line/load reactors. Is the premise of these to simply control the impedance seen by the source so as to allow for more power quality, and reliability? or to correct power factor etc on a load by load basis?
input appreciated
1 - to reduce the available fault current seen by the chiller
2 - to increase the AIC of the chiller.
Our recommendation as a firm is going to end up being to supply new VFD starters for these chillers. After looking into using a line reactor to reduce the fault current seen by the chiller, an app engineer told me that these reactors can only be used when a VFD is existing and will reduce the seen fault current by max of 5%. I really have no feel for these reactors and what they do, and when you would want to use them by and large.
I have heard many times of line/load reactors. Is the premise of these to simply control the impedance seen by the source so as to allow for more power quality, and reliability? or to correct power factor etc on a load by load basis?
input appreciated